Estimate the DG set rating in kVA for a connected load of 1600 kW with a diversity factor of 1.88. Consider 85% loading and power factor as 0.8.

In Science | Asked by sathees2
Best Answer
Connected load : 1600 kW
Diversity factor : 1.88
Maximum demand : 1600/1.88 = 850 kW
% loading : 85%
Set rating : 850 / 0.85 = 1000 kW
At 0.8 pf, rating : 1250 kVA